What damage can water inside copper wire cause?
Here is the problem I came accross ...
An underground lateral installed in ridged metal conduit to a riser up a utility pole where the POCO connects the type THHN/THWN at the top without any form of drip loop to prevent water from entering the wire.
So, we have the inside of the cable full of water from the point of connection at the top of the pole to the lugs in the meter, and the inside of the ridged conduit will have water in the low points underground.
Well, there seems to have been an insulation failure of one of the wires in the riser, causing a burn out on one of the hot legs to the ridged.
We just had 2 days of freezing temps (0 degrees F) and then 38 degrees on the morning of the fault. Could the freezing of the water inside the wire and subsequent thaw have caused the insulation to fail?
shortcircuit
|
|
|
|
Joined: Dec 2004
Posts: 1,064
Member
|
I would tend to think nothing.....
The insulation on the wire should be rating for it's purpose. Most pipes underground have water in them anyway. Did the rigid rust and collaspe, like I have seen, cauing the fault?
Dnk...
|
|
|
|
Joined: Jun 2004
Posts: 613
OP
Member
|
I don't think that the water in the pipe was any problem. But the water in the wire may have been the cause.It is tough to tell after the burn out what was the actual cause, for me.
There was no corrosion of the conduit and minor damage to the ridged at the fault location. But the wire burnt clear through.
Is the wires insulation (THHN/THWN) tested for the conditions that I've described...with water on the inside of the wire in freezing temps?
shortcircuit
|
|
|
|
Joined: Jul 2002
Posts: 680
Member
|
Is it possible when water gets thru the insulation, it becomes a conductor between rigid steel pipe and copper. You end up with a cathode and anode?? ..
|
|
|
|
Joined: Dec 2005
Posts: 64
Member
|
There should have been a drip loop, or some other protection.
You wont keep water out of the undergound portion, but if it is flowing up into the panel, then it is a problem.
|
|
|
|
Joined: Jan 2004
Posts: 615
Member
|
I would think it is more likely that there was a nick in the insulation from installation. If you're thinking that water would creep down between the copper and insulation, I would think that surface tension of the water would keep it from running, unless I'm not understanding surface tension correctly.
Another thing, I don't know if the expansion ratio of water to ice would be enough to split the insulation from the inside out. If water could get all the way down the insulation it would only be a small amount. Although the plastic would probably more brittle at these lower temperatures, I wouldn't expect it to split like a copper water pipe.
[This message has been edited by Jps1006 (edited 12-17-2005).]
|
|
|
|
Joined: Jun 2004
Posts: 613
OP
Member
|
There must have been a nick in the wire which led to the failure.
But,there was water inside the wire, which dripped out when the remainder of the damaged cable was removed from the conduit.
shortcircuit
|
|
|
|
Joined: Dec 2005
Posts: 64
Member
|
jps, i too have seen water run inbetween the insulation and the conductor. if one side like on a pole is way above another side, like in a panel. water will bubble up in the panel. to prevent this a drip loop is needed.
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
The water in the conductor could very well have split the insulation when it froze. The cold temperature makes the insulation brittle and the 10% expansion caused when the water becomes ice could cause this type of problem. Remember that the manufactures say that this type of cable should not be handled below 15°F to prevent insulation cracking when you are installing it. It can be used, but not handled (moved) at lower temperatures. This connector is sometimes used to solve this problem. The shrouded part of the barrel goes over the insulation, and this prevents water from entering the conductor. I worked on a job where we were replacing 5kV conductors from the service drop to the switch gear. The joints at the switch gear bus were taped and when we took off the tape, we got about a quart of water out of each conductor. When we replaced the conductors we used the shrouded lugs. Don
Don(resqcapt19)
|
|
|
|
Joined: Jul 2002
Posts: 8,443 Likes: 3
Member
|
Any sort of moisture getting into copper wires, will at the first stage cause them to darken. This is the first stage of oxidisation. The second stage is where the formation of "Verdigris" takes place and the copper starts to break down. If the 2nd stage is allowed to continue, it will eat right through the conductor. I've seen a lot of pre-wired A/C units where the ends of the cables are not sealed, strip the wire back and you can almost tell how long the wire has been exposed to the elements for. The water/moisture moves up the wire/cable by Capillary Effect.
|
|
|
Posts: 28
Joined: February 2011
|
|
|
|