We are currently doing a project with a massive amount of pvc coated rigid conduit.
Here in Maryland it is referred to as
" Rob Roy" No one is sure why - Do any of you know ?

#59798 12/14/05 09:37 PM
Joined: Dec 2003
Posts: 886
H
Member
It's the name of one company that makes the stuff. robroy.com

Guess it's called that just like Scotch tape, Xerox or Band Aid is generic for every other brand.

-Hal

#59799 12/14/05 10:41 PM
Joined: Dec 2005
Posts: 64
J
Member
romex, bx, madison strap, unistrut, minerlac strap...... the list goes on.

#59800 12/15/05 04:11 PM
Joined: Dec 2004
Posts: 94
T
tkb Offline
Member
RobRoy is one of the brands also Permacote.

I have installed a lot of it.
Have you install it before?
I could share some tips if you would like.
What are you using to cut and thread it with?

#59801 12/15/05 06:09 PM
Joined: Dec 2003
Posts: 886
H
Member
One of the trade mags a couple of months back had an in depth article on cutting and threading this stuff.

You can't just use regular threading tools. The hole in the die head has to be enlarged to accommodate the extra diameter of the pipe due to the PVC coating. There are also padded vice jaws so you don't damage the coating.

-Hal

#59802 12/17/05 07:04 PM
Joined: Jan 2005
Posts: 316
L
Member
I have worked with this stuff before. It can be a real pain if you let it. We have no problem threading it, we bought some steel plates that go between the conduit and the jaws on the threader to prevent damage to the coating. The only problem we seem to be running into is the seals in our benders are starting blow. I think it is more of a benders age problem then a pvc coated rigid problem. But any ideas are more then welcome. Thanks

#59803 12/17/05 11:24 PM
Joined: Apr 2002
Posts: 257
M
Member
We did a sewage plant and used pvc coated rigid. The company that sold us the conduit provided a threader for upto 4" coated and some special dies for smaller pipe (3/4 & 1")for our pony threader. Depending on how big your job is, maybe you could do the same.