ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 516 guests, and 17 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
#59709 12/13/05 12:51 PM
Joined: Oct 2004
Posts: 55
I
Member
I need a 250 - 300 amp AC relay and have checked Allen-Bradley and a few others. Can anyone tell me where a high current AC relay can be obtained?

#59710 12/13/05 02:34 PM
Joined: Sep 2001
Posts: 806
N
Member

#59711 12/13/05 05:06 PM
Joined: Jan 2005
Posts: 155
D
Member
Lighting contactors are available up to 400a and diffinite purpose contactors shoulde be also. I'm assuming you're talking about 480vac. Usually when one inquires about a product one includes the voltage rating of the device in question, the numer of poles, the type of load, latching of magnetically held, coil voltage as will a the current requirement. Otherwise, should an answer be provided based upon limited information the answer is likely to be incorrect for the actual application.

#59712 12/14/05 12:35 AM
Joined: Oct 2004
Posts: 55
I
Member
Ask a general question, get a general answer.
My mistake, I should have given the application.

This is for a generator transfer switch. So it would be a double pole, double throw, and rated at preferably 250 amps continuous. Normal residential voltage 120/240.

Thanks!

#59713 12/14/05 02:53 AM
Joined: Oct 2004
Posts: 132
M
Member
Whoa...you're trying to build your own transfer switch??!! Whatever you build is not going to be listed for the application, and won't be as relaible as a purpose-built transfer switch. This is not something you want to mess around with! Besides, you will have a hell of a time finding a double throw, 250A relay!

May I suggest a real, listed transfer switch, a reliable company is ASCO, check out what they have here http://www.ascopower.com/Products/ATS/atsmenu.html

be safe!

mike

#59714 12/14/05 10:47 AM
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
FYI, relay contacts are usually limited to 10A and sometimes as high as 20A. Above that current rating the devices are usually called contactors. Normally closed contacts are not usually available above 100A.

For 300A non-life-safety semi-automatic transfer switches some fire truck manufactures use mechanically interlocked 400A contactors, one coil wired to the on-board generator and the other coil wired to shore power.

For home-built applications stick with a listed commercial transfer switch especially if you need engine start and exercise functions.

#59715 12/14/05 11:24 AM
Joined: Oct 2004
Posts: 55
I
Member
The service is 225 amps for the house. The generator/transfer switch are rated at 100 amps. Generator controlled circuit breakers will drop enough circuits in the house to keep the generator happy.

It sounds like a contactor rated for 225 amps would work to disconnect the mains service before the generator fires up, then let the transfer switch relay dump the generator to the house feeders once the warmup period has elapsed. I just thought an external relay (or contactor) rated for the full normal service current would negate the need for two separate electrical items.

The transfer switch has all the bell and whistles, it just isn't built into the generator as some are. I'm well aware of the safety issues! Thanks for the response!

#59716 12/15/05 12:17 AM
Joined: Feb 2005
Posts: 693
L
Member
It sounds like you want to use this relay so you can use a 100a TS instead oif a 200a one. I have a feeling that a 100a TS and a 200a contactor will cost more than the 200a TS will.

I suggest getting the proper TS and save the 100a TS for a 100a service.


Larry Fine
Fine Electric Co.
fineelectricco.com
#59717 12/15/05 09:23 PM
Joined: Apr 2002
Posts: 7,382
Likes: 7
Member
Sounds like what you are trying to accomplish with individual components is classic 'over-engineering'.

A manufactured transfer switch, automatic, or perhaps manual would be the 'preferred method'.

Your statement "The service is 225 amps for the house. The generator/transfer switch are rated at 100 amps. Generator controlled circuit breakers will drop enough circuits in the house to keep the generator happy."

Please explain what a 'generator controlled circuit breaker' is??

John


John
#59718 12/15/05 10:01 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
Chief, you are looking for one of these.... http://www.asco.com/cgi-bin/redirect.pl?/product.html

I am afraid to think of what could go wrong in the possible reconnection of the POCO and your generator due to relay contacting at the wrong time. Unless you have a fool proof make before break circuit, I would not want the liability. Also what will you be doing with the neutrals?


Mark Heller
"Well - I oughta....." -Jackie Gleason
Page 1 of 2 1 2

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5