is it acceptable to use split bolts to connect from the primary side of a main breaker to service another main breaker in a seperate panel. let me explain, from the meter socket we feed a 200a main breaker panel, an additional garage was added with a 100a main breaker panel. could i use split nuts to terminate and supply power to the second panel or just put another 100a breaker in the first panel to feed the second 100a main breaker in the second panel? In this configuration both panels would have a paralle feed from the meter. Does this violate any code?
|
|
|
|
Joined: Jun 2004
Posts: 220
Member
|
I would put another breaker in the main panel and feed out to the garage. you would save time and IMO have a more secure connection. Is there some reason you wanted to do it this way, like no more spaces in the main panel? As far as violating any code, I would want to know how far from the main it is, you might be able to use the tap rule.
[This message has been edited by trekkie76 (edited 12-07-2005).]
|
|
|
|
Joined: Jun 2001
Posts: 161
Member
|
I've been having a brain block on this one... When you run wires from the meter to the building main breaker it is called a service conductor, right? What is the wire set called when you run from a new 100A breaker in the main panel to another building, as in the suggestion from trekkie76? Feeder? Lateral? Branch circuit conductor? I want to find out to apply the proper rules from the code to see if I can run them inside or if I need 2" concrete or keep them outside... (Some days there's just too many pages in the code... ;-)
Mike Wescoatt
|
|
|
|
Joined: Feb 2005
Posts: 693
Member
|
I would see a problem with placing 300 amp's worth of main breaker on a feeder sized for 200. Use the breaker.
Larry Fine Fine Electric Co. fineelectricco.com
|
|
|
|
Joined: Jul 2004
Posts: 9,932 Likes: 34
Member
|
Any connection on the line side of the service disconnect is a service entrance conductor and would have to follow SE rules. It also adds to the size of the service as Larry points out. Installing this as a feeder (on the load side of the service disconnect) is a safer option with less potential problems.
Greg Fretwell
|
|
|
|
Joined: Jan 2005
Posts: 91
Member
|
I think that code section that your question refers to is 230-40 exception #1.
You've given us breaker sizes but I'm curious about the calculated or actual loads served by both panels - 230-23 (a) & 230-31(a).
Another approach would be to come off the load side meter lugs. While permissable you won't have the added piece of mind that having a CB on the conductors would give you.
[This message has been edited by Helectric (edited 12-07-2005).]
|
|
|
|
Joined: Dec 2005
Posts: 64
Member
|
Where are you planning to find a meter with lugs rated for more than one wire?
The biggest concern I would have is stripping the current wires to attach that split bolts as they are live.
|
|
|
|
Joined: Aug 2001
Posts: 335
Member
|
jwhite: I did one that had a 400a meter can, 350 Cu thru the mast to the POCO. In the meter can we removed the single lugs and put in doubles. We fed two separate panels, one in the house and one in a garage. AHJ had no prob with changing the lugs. (in that area the homeowner owns the meter can, it's not provided by POCO)
|
|
|
|
Joined: Jan 2005
Posts: 91
Member
|
JWhite & Steve,
Yes, this is done in my area as well. I think that you can even order meter cans with studs only and then install the desired lugs yourself. If I remember correctly, the code allowed this practice until the 70's then it was taken out for about 24 years. I'm not sure but I think it (230-40 exception #1) first reappeared in the 2002 code.
[This message has been edited by Helectric (edited 12-07-2005).]
|
|
|
|
Joined: Dec 2003
Posts: 751
Member
|
If you tap the service conductors ahead of the main, these are still service conductors, and are subject to all the rules of services. You cannot run service conductors through building #1 to feed building #2. (230.3) Either make your connection outside the building (10x10x4 J-box) or feed through a CB, as discussed.
[This message has been edited by earlydean (edited 12-07-2005).]
Earl
|
|
|
Posts: 806
Joined: October 2004
|
|
|
|