Safety at heights?
0 members (), 228 guests, and 10 robots.
#59194 11/29/05 07:11 PM
Q
qopanel Offline OP
My boss and I are having a disagreement with the sizing of a raceway bond. We have a 600amp service, with Parallel 350's fed underground to a distribution panel through pvc. I,m saying we need to have 1/0, and he is telling me #1. I'm a little confussed on where to find the sizing of this conductor. Should it be based on 250.66?
#59195 11/29/05 07:21 PM
Q
qopanel Offline OP
Never mind....I had a brain fart and forgot to look a little further...250.122. I lost. Now I owe the boss lunch.
#59196 11/29/05 08:27 PM
Tom Offline
Now you've got me confused. Why are you bonding PVC? If the parallel 350's were copper and in a metal conduiit, the bonding conductor would be 2/0.
Or, are you bonding a conduit that is after the service disconnect & overcurrent device?
Tom
Few things are harder to put up with than the annoyance of a good example.
#59197 11/30/05 08:04 PM
Q
qopanel Offline OP
I am bonding heavy wall conduit stubbed down, then changing to pvc underground, then back up in heavy wall again. And yes it is after the overcurrent device.
#59198 11/30/05 08:54 PM
Tom Offline
Yup, you owe the bossman a lunch. You going to get him something good?