ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 259 guests, and 15 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#59194 11/29/05 07:11 PM
Joined: Jul 2002
Posts: 17
Q
qopanel Offline OP
Member
My boss and I are having a disagreement with the sizing of a raceway bond. We have a 600amp service, with Parallel 350's fed underground to a distribution panel through pvc. I,m saying we need to have 1/0, and he is telling me #1. I'm a little confussed on where to find the sizing of this conductor. Should it be based on 250.66?

#59195 11/29/05 07:21 PM
Joined: Jul 2002
Posts: 17
Q
qopanel Offline OP
Member
Never mind....I had a brain fart and forgot to look a little further...250.122. I lost. Now I owe the boss lunch.

#59196 11/29/05 08:27 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
Now you've got me confused. Why are you bonding PVC? If the parallel 350's were copper and in a metal conduiit, the bonding conductor would be 2/0.

Or, are you bonding a conduit that is after the service disconnect & overcurrent device?

Tom


Few things are harder to put up with than the annoyance of a good example.
#59197 11/30/05 08:04 PM
Joined: Jul 2002
Posts: 17
Q
qopanel Offline OP
Member
I am bonding heavy wall conduit stubbed down, then changing to pvc underground, then back up in heavy wall again. And yes it is after the overcurrent device.

#59198 11/30/05 08:54 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
Yup, you owe the bossman a lunch. You going to get him something good?