bot540 Offline OP
If you already upsized the wire for voltage drop would you have to further derate the wire if you have more than 4 current carrying conductors? Do the calculations compound?
Jesus may have been a capenter,but God was an electrician.Genesis1:3
Cow Offline
Bob Offline
First caculate the load.
Size the wire for the load.
Derate per the table 80%. This will give you a larger conductor. Caculate the VD using this conductor.
If you have to go larger you do not derate again.