1 members (Scott35), 391 guests, and 10 robots.
bot540 Offline OP
If you already upsized the wire for voltage drop would you have to further derate the wire if you have more than 4 current carrying conductors? Do the calculations compound?
Jesus may have been a capenter,but God was an electrician.Genesis1:3
Cow Offline
Bob Offline
First caculate the load.
Size the wire for the load.
Derate per the table 80%. This will give you a larger conductor. Caculate the VD using this conductor.
If you have to go larger you do not derate again.