ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 507 guests, and 15 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Sep 2004
Posts: 174
B
bot540 Offline OP
Member
If you already upsized the wire for voltage drop would you have to further derate the wire if you have more than 4 current carrying conductors? Do the calculations compound?


Jesus may have been a capenter,but God was an electrician.Genesis1:3
Joined: Jul 2005
Posts: 33
C
Cow Offline
Member

Joined: Feb 2002
Posts: 182
B
Bob Offline
Member
First caculate the load.
Size the wire for the load.
Derate per the table 80%. This will give you a larger conductor. Caculate the VD using this conductor.
If you have to go larger you do not derate again.


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5