#5871 12/12/01 04:49 PM
dom Offline OP
What does the dual rating listed on circuit breakers mean? (60/75) Is it just indicating a range of wire sizes that will legally fit into the terminal, or is there more to it?
If there is a choice, most people would probably choose to use the 75 deg rating.
thank you
#5872 12/13/01 12:54 AM
This should indicate that the terminal is listed for use at either temperature ampacity. If the teminal was only listed for use with a 60 degree termination it would affect the wire size you could use to achieve the required ampacity. See Section 310-10 and the associated Tables to see the affect of the different ampacities in the different temperature columms.