Safety at heights?
1 members (Scott35), 235 guests, and 27 robots.
#58063 10/28/05 12:20 AM
Tripp Offline OP
There was recently a thread that dealt in part with this topic, but for the life of me I cannot find it. My question is: WHAT IS THE DEFINITION OF A TAP CONDUCTOR? I find it nowhere in the NEC. More specifically, when you terminate a #8 copper in a box for a raqnge recept, can you pigtail the grounds to a smaller AWG? Is this a "tap"?
#58064 10/28/05 08:59 AM
You will find your definition in 240.2.
Also, what you describe is not a tap, it is an undersized equipment grounding conductor [Linked Image]
Ryan Jackson,
Salt Lake City
#58065 10/28/05 03:27 PM
Tripp, you're hunting for table 210.24....
Also study 240.5 particularly 240.5(2)
Also study 210.19 (A)(3) exceptions #1,#2
Also study 210.19 (A)(4) exception #1 (c)
These tap conductors are limited to 18 inches.
Tesla