ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 516 guests, and 17 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 3 of 3 1 2 3
#57938 11/07/05 06:02 PM
Joined: Jun 2005
Posts: 821
S
Member
According to Art. 250.104(b), as several of you have stated, the gas pipe is required to be bonded, however, the equipment grounding conductor can be used for this purpose.


That is how I've always understood it. Whether the furnace/ boiler is wired in E.M.T. or MC cable, the EGC is sufficient to bond the gas piping in the house.

#57939 11/07/05 07:59 PM
Joined: Aug 2005
Posts: 265
S
Member
In BC, we must bond the gas line.

A few years back I was installing a service on a new mobile home. The gas company had installed their line (metal) from the street, and capped it off without a meter. The gas installer hadn't yet run the pipe out from the furnace. Rather than making a 2nd trip back to bond the inside gas line, I decided to bond the incoming line from the street....ended up getting an irate call from a foreman at the gas company saying it was a big NO NO to bond their line as they run a small current through their old metal lines for corrosion. The meter has an isolation point so by bonding on the "load" side of the gas meter, the bond is isolated from the "line" side.


Sixer