Electricians revenge
2 members (Scott35, gfretwell), 42 guests, and 12 robots.
#57154 10/05/05 11:50 PM
Well the same thing with the grounding conductor, even if it's 4 grounds in there, it's still 1. I guess the clamps will apply the same concept.
#57155 10/06/05 01:42 PM
I believe the answer is 10 #12 conductors.
Peter
Peter
#57156 10/06/05 03:30 PM
314.16 (B) (4): For each yoke or strap containing one or more devices or equipment, a double volume allowance in accordance with table 314.16 (B) shall be made for each yoke or strap based an the largest conductor connected to a device(s) or equipment supported by that yoke or strap.
Simply stated you count 2 wires for each yoke. [Linked Image]
Chris
#57157 10/06/05 05:15 PM
since the grounding conductor on the device originates outside the box it is counted a .....1, this counts as an additional EGC...250.146 and 316.16(B)(5) any jumpers that stay in the box are not counted
total is therefore ....11
#57158 10/06/05 06:32 PM
togol,
Good observation, but I think you are referring to an additional IG grounding conductor.
I count...10
[This message has been edited by Redsy (edited 10-06-2005).]
#57159 10/06/05 07:31 PM
Redsy.
....yep there it is,
I also typed the wrong reference ....should be ....314.16 (B)(5)
but it does seem to contradict ......(1) of the same section !