ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 228 guests, and 10 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 2 of 3 1 2 3
Joined: Aug 2005
Posts: 89
D
Member
Don't those window A/C units only draw in the range of 4A-8A, depending on size?

Joined: Jun 2005
Posts: 49
G
Member
Computers, lights, tv's (for some people), a/c's (as mentioned), refrigerators, stereos... I'm sure the list can be expanded, but all of these things are often on for more than 3hrs. And a lot of homes have central air, those units can get a little big. But, the only real continuous load on an a/c is the fan. The compressor only runs when the a/c cycles which can vary in frequency depending on the conditions.

So, as DS has asked, in residential (or any application for that matter) how do you determine "continuous loads"? Or do you just forget about it and do it anyway regardless of the code?

Joined: Aug 2005
Posts: 89
D
Member
So, even if the total load isn't close to the rating of the circuit breaker, or percent thereof, it must be derated anyways?

Joined: Jun 2005
Posts: 49
G
Member
derating is for the conductors, not the breaker. you're giving the same current a larger wire to run on, but the current is the same for the breaker. the issue is heat dissapation.

Say you're running a 20A circuit on #12 wire, but due to derating you have to drop down to #10, you're still running a 20A circuit with a 20A breaker. And as far as I can tell, the derating is only applied where you have the wires running together, so you can have #12 in free air, but have #10 in conduit for the same circuit. Am I wrong here?

Joined: Nov 2000
Posts: 2,148
R
Member
The "adjustment factor" (derating) changes the maximum permitted ampacity of the conductor. The size of the overcurrent protective device cannot not exceed the maximum permitted ampacity of the conductor.
Don


Don(resqcapt19)
Joined: Feb 2002
Posts: 840
C
Member
Quote
So, as DS has asked, in residential (or any application for that matter) how do you determine "continuous loads"?

In reality, there are almost no continuous loads in a dwelling unit.

Think of it this way: How many circuits are loaded up to their full ampacity for 3 hours or more? I would say none.

Peter


Peter
Joined: Aug 2005
Posts: 89
D
Member
I see. Would derating apply to conduit as well?

Joined: Jun 2005
Posts: 49
G
Member
well, once you've derated, you're now dealing with larger wires, which will require larger conduit.

Joined: Jul 2005
Posts: 46
R
Member
Derating does apply to conduits.

Also derating is done when you have more than three current carring conductors, regardless if it is a continuous load or not.

Keep in mind that you can use the temp rating of the wire for derating. So for THHN you can use the 90 degree column of 310.16 for you derating. If you notice that column lists the ampacitiy of # 12 as 30 amps. [Linked Image] [Linked Image] [Linked Image]

Chris

Joined: Aug 2005
Posts: 89
D
Member
Another question, let's say you've caluclated the derating of the circuits and come up that you'd need to use #10 wire. Does this mean that the entire install needs to be in #10 wire, or does it mean that only the homeruns that'll end up in the gutter box need to be #10 wire?