Electricians revenge
1 members (Scott35), 34 guests, and 20 robots.
#55760 09/05/05 11:32 PM
I've been through the code book up and down. I can not find the answer to this question. Someone asked me if it was true that if a 4"sq han more than 3 conduit in it , it would not need support. I have seen boxes like this before. I just can not find it in the book. Any help please. Thanks.
#55761 09/06/05 12:27 AM
314.28(E) Raceway Supported Enclosure, Without Devices, Luminaires (Fixtures), or Lampholders. An enclosure that does not contain a device(s) other than splicing devices or support a luminaire(s) [fixture(s)], lampholder, or other equipment and is supported by entering raceways shall not exceed 1650 cm3 (100 in.3) in size. It shall have threaded entries or have hubs identified for the purpose. It shall be supported by two or more conduits threaded wrenchtight into the enclosure or hubs. Each conduit shall be secured within 900 mm (3 ft) of the enclosure, or within 450 mm (18 in.) of the enclosure if all conduit entries are on the same side.
Exception: Rigid metal, intermediate metal, or rigid nonmetallic conduit or electrical metallic tubing shall be permitted to support a conduit body of any size, including a conduit body constructed with only one conduit entry, provided the trade size of the conduit body is not larger than the largest trade size of the conduit or electrical metallic tubing.
handbook commentary
Boxes are not permitted to be supported by rigid raceways using locknuts and bushings. Enclosures without devices or luminaires, however, are considered to be adequately supported, provided the conduit is connected to the enclosure by threaded hubs and the threaded conduits enter the box on two or more sides and are supported within 3 ft of the enclosure. A box is not permitted to be supported by a single raceway.
[This message has been edited by gfretwell (edited 09-06-2005).]
#55762 09/06/05 06:54 AM
I do not know how it overlooked that. Thanks much.
#55763 09/06/05 09:08 AM
I think that code reference was supposed to be 314.23, not 314.28.
Ryan Jackson,
Salt Lake City
#55764 09/06/05 10:38 AM
For the purposes of this application, does the threaded hub have to be part of the box, or is the use of a product like a Meyres Hub permitted?
Don