ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 534 guests, and 33 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 2 of 2 1 2
#55239 08/22/05 08:40 PM
Joined: Sep 2003
Posts: 650
W
Member
For what its worth, I am certain that lethal voltages _can_ occur on CT open secondary. In particular, with the secondary open and reasonable primary current flow, I'd bet the core saturates, causing considerable harmonic content in the secondary voltage. I would not be surprised to see extremely high peak voltages with moderate RMS voltages.

I tried to estimate the secondary voltage given a 1 square inch core and 2 Tesla saturation and 80 turns; depending on the saturation, I could see the peak output voltage anywhere from 60V on up. It would be entirely reasonable to get high enough voltage to arc over, followed by enough current to sustain the arc.

-Jon

#55240 08/22/05 11:14 PM
Joined: Aug 2001
Posts: 599
N
Member
Here
is a picture of damage from an open CT circuit. The terminal on the upper right that is not connected was jammed behind the shorting block from the factory. We energized this gear on a weekend change over. When we started feeding load I heard arcing and smelled that awful smell of something electrical burning. [Linked Image]