1 members (Scott35), 381 guests, and 13 robots.
#54597 08/02/05 09:37 PM
Is this OK?
In a school, there is a 150 KVA transformer (480V delta Primary / 120/208Y secondary) installed 6" away from a MLO panel.
The MLO panel is fed from the MDP (located in an electrical room on the other side of the building) via a 400A Fused switch.
The transformer is fed from the feed-thru lugs in the MLO panel with 4/0 copper in flex.
The transformer then feeds a 120/208Y panel (6" away) with paralleled 4/0 copper in flex terminating in a 400A main breaker.
Does this meet all requirements of articles 240.21 and 450? (2005 NEC)
#54598 08/03/05 06:01 AM
Sure. [Linked Image]
The primary current of the 150 KVA transformer is about 180 amps.
Table 450.3(B) allows the primary overcurrent protection to be 250% of the primary current when secondary protection is provided.
180 x 2.5 = 450 amps.
On the secondary side we are allowed 125% and we can round up to the next standard size OCP.
The secondary current of a 150 KVA transformer is 416 amps.
They could have gone higher than 400 amps on the secondary side. [Linked Image]
#54599 08/03/05 06:51 AM
How and where does the GEC terminate?
Dnk......
