I was asked this today due to a wrong spec on a job. The shade company required a 12-2 romex at each window shade location for power, so I did it. I went there today to start the install and reading the shade info it needs a 12-3 romex to work. The shade guy wants to use the ground conductor as a neutral and I told him no way no how. I am just thinking now though what is the real reason behind this. Safty because no ground? The current on the neutral now is not insulated on it's return trip?
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
"Safty because no ground? The current on the neutral now is not insulated on it's return trip?"
YES And YES (Could also cause ground / neutral contact in a metalic box - after the main.)
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
Oh, been in this situation before...
If its you fault... Look into romote control ones, cheaper than re-finish sometimes.
Not your fault, T&M C/O!
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
Joined: Apr 2002
Posts: 7,383 Likes: 7
Member
|
OK, the bare conductor will be carrying the current as you said, and basically be "live" to a grounded object, box, etc; or a person.
YES it is a saftey issue, yes, it is NOT NEC compliant, and yes you are 100% right saying 'no way'.
I have seen instances where EMT was used as the 'neutral' for a 30 amp, 120 volt circuit that consisted of ONE 'hot' conductor. Yes, it worked, but the setscrew couplings were not tightened properly and started arcing. It almost caused a fire, as the EMT was installed on a wall that had clothing racks mounted on it.
Some of the 'old timers' used to say "gyp the ground" when you had a 'open' neutral to restore the circuit; heck I saw BX armour that was 'live' arcing on suspended ceiling grid.
You're right; illegal, unsafe, and not to be done.
John
John
|
|
|
|
Joined: Jun 2005
Posts: 821
Member
|
Oh, what the heck, as long as it works, right?
*rollseyes
What "electrician" walks away from a job thinking it's ok to use EMT as the grounded conductor?
|
|
|
|
Joined: Oct 2004
Posts: 265
Member
|
Er, misread something
[This message has been edited by dmattox (edited 07-29-2005).]
|
|
|
|
Joined: Oct 2003
Posts: 259
OP
Member
|
I know not to do it and will get paid to fix it. The shade system is part of a larger system that is all tied together for controlling lighting, video and sound systems so doing anything but snaking in new cables will not work.
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
I know not to do it and will get paid to fix it. Good choice. Do not listen to "The Shade Guy" he is not NEC trained and he is not on the hook if the electrical portion of the shades causes a problem. Would you tell him how to hang drapes?
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Oct 2000
Posts: 2,749
Member
|
Because, 334.108 Equipment Grounding.
In addition to the insulated conductors, the cable shall have an insulated or bare conductor for equipment grounding purposes only.
Joe Tedesco, NEC Consultant
|
|
|
|
Joined: Oct 2003
Posts: 259
OP
Member
|
Thanks guys. I know not to do it just wanted to make sure I was right in my reasons, besides the code.
|
|
|