I have a contactor supplied by a plumber for a misting system. It is a Square D 8910DPA. Basically a 3 phase/1 phase contactor with a 24 V coil. It didn't have a wiring diagram and I haven't dealt with contactors before. My question is how do I get the coil to fire? Do I need an external power source?
#54170 07/21/05 01:32 PM
Sounds like you need a 24V source to energize the coil, plus some way to control (ON/OFF) the 24V. You also need to confirm the 24V you're talking about is 24VAC as opposed to 24VDC. A 24VAC supply is pretty easy to provide, a 120V circuit feeding a 120V to 24V transformer. The 24V side of the transformer probably needs fuse protection sized to the transformer rating.
Radar
#54171 07/21/05 03:03 PM
You could also explore the possibility of swapping the coil out to the voltage you are controlling (208?, 480?). Most contactors will have interchanageable coils of many different voltages.
Earl
#54172 07/21/05 03:09 PM
just checked out the grainger site. There is a 120 volt coil kit you can purchase for $64.
Earl
#54173 07/21/05 06:08 PM
Sometimes the controller/timer for the misting system or sprikler system will have a 24 volt output for the pump contactor.
You should find out how they plan on controlling this before spending any money on transformers etc.
#54174 07/21/05 11:13 PM
K
kinetic Offline OP
Thank you for the help. I thought I would need an external power source like you mentioned Radar. I didn't feel like experimenting with the contactor and risk blowing it up or causing bigger problems. The mister is 240V 1 phase and I was going to ask the plumber to get a different contactor with a 240V coil but he left town for vacation this week. Easier for me to get a simple multi-tap transformer and be done with it. The other misting systems I helped install all had internal controllers but for some reason this one did not.
#54175 07/21/05 11:16 PM
One of my favorite new "Candid Camera" episodes showed what happened when they connected the misters at a supermarket produce case to a motion sensor. Customer approached produce, mister fired...:-)
#54176 07/22/05 11:03 AM
K
kinetic Offline OP
Hmmmmmm.....you trying to give me ideas? This guy has a pretty good sense of humor. He might actually like that.
#54177 07/22/05 11:23 AM
The contactor needs to have the single phase Hot 'snaked' through the contacts to equalise the overload 'heaters' if fitted- see my question posed 04 26 2005 under 'Motor Starter' ( currently on p. 9 ) for the good advise I got. Will a 240-24V transformer, plus casing, be cheaper than a new 240v coil?