drgnz23 Offline OP
I having a discussion with one of the older guys about conductors in a 1/2 conduit. I look it up in the code book but its kind of confusing. For example (SIMPLE) 1/2 emt only 9 thhn wires .Is one of those a ground?
#53624 06/30/05 06:55 PM
The wire fill is a physical count of the wires in the raceway. What function the wires serve does not enter into this.
Don
Don(resqcapt19)
#53625 07/01/05 11:12 AM
This information is based on Table 1 in Chapter 9 of the NEC, which specifies maximum raceway fill:
53% max for a single conductor in the raceway (i.e. - grounding conductor)
31% max for two conductors
40% for 3 or more conductors
The unused volume of air space within the raceway is needed for cooling of the conductors which tend to warm up due to conductor heating caused by current flow thru the circuit conductors. Overstuffing a raceway, aside from making for a difficult pull, would contribute to conductor overheating by reducing the cooling medium.
Radar
There are 10 types of people. Those who know binary, and those who don't.