#5297 11/13/01 09:06 PM
Joined: Oct 2000
Posts: 5,392
S
sparky Offline OP
Member
situation;
almost 500' of 350kcmil triplex urd al. for UG lateral [Linked Image]
problem;
sparky did'nt eat his wheaties.... [Linked Image]
fix...
whip together a quick deer sling out of NM and a few rags for a shoulder cushion, attach pvc via bell end by way of rubber bungee for quick connect/disconnect. Drag over triplex, hands free to pick up and place triplex. Glue on one piece on @ a time.
[Linked Image]

#5298 11/13/01 09:33 PM
Joined: Oct 2001
Posts: 45
W
Member
I'm glad that I am not the only one who works for a living!! Way to go!! My helper and I just did a similar job with 100ft of two 500mcm and one 350 for a 400amp service. We slipped the 3" pvc over it. Didn't even think of the sling idea. Thats a good one.

#5299 11/13/01 09:38 PM
Joined: Oct 2000
Posts: 5,392
S
sparky Offline OP
Member
well Hi there WireWrestler!
welcome to the forum where idea's are traded.
[Linked Image]

#5300 11/13/01 09:42 PM
Joined: Oct 2001
Posts: 45
W
Member
Glad to be here. I have been reading the forums for a long time and I have learned a lot from everyone. I decided to quit being lazy and participate.

#5301 11/13/01 10:17 PM
Joined: Nov 2000
Posts: 2,148
R
Member
What about 300-18(a)???
Don(resqcapt19)


Don(resqcapt19)
#5302 11/14/01 07:11 AM
Joined: Oct 2000
Posts: 5,392
S
sparky Offline OP
Member
Don,
i'm aware of 300-18(a) , and would comment that the intent is for the conductors protection, which i am actually taking better care of here, than if i were to set up pulling stations etc.

#5303 11/14/01 10:48 AM
Joined: Nov 2000
Posts: 2,148
R
Member
Sparky,
And how are we supposed to pull out the conductors and replace them if needed at a later time. If you can't pull them in the first time without damage, you can't repull them without damage. One of the reasons for 300-18(a) if the ability to make future changes or repairs.
Don(resqcapt19)


Don(resqcapt19)
#5304 11/14/01 12:39 PM
Joined: Mar 2001
Posts: 2,056
R
Member
Don,
It seems to me that with the proper(expensive) equipment, this pull would have been able to be accomplished. Sparky just didn't have the equipment. The next guy may need it regardless of how it was originally installed.
Sparky,
Why not direct-bury?
BTW,
How often should pull boxes be installed?

[This message has been edited by Redsy (edited 11-14-2001).]

#5305 11/14/01 12:53 PM
Joined: Nov 2001
Posts: 280
M
Member
Sparky;
500 feet you say, how do you pull it, I mean after the 'Deer-sling', do you use a Tow-motor or a pick-up with 4 x 4 ?

#5306 11/14/01 05:00 PM
Joined: Oct 2000
Posts: 5,392
S
sparky Offline OP
Member
One of the reasons for 300-18(a) if the ability to make future changes or repairs.
Don, this is true. However the utilities engineers here would allow me to install this @ over 600', no UG boxes at all, and they engineered it! The answer is, you dig it up again. Please realize that I am competing with those that have buried service laterals 12" deep in sewer pipe here,etc, etc ( many stories..) None of this ever gets an inspector, and the utilities regularly will hook up time bombs for any of the Clampet clan.
Am I any more guilty in the real world than those who would hide behind 90-4?

Sparky,
Why not direct-bury?

Redsy;
They did away with direct burial, not that it stops homeowners, excavators, etc here.
And no, I don't have the equipment, i'm one man, one van feedin'the fam,that's it. If i don't say so myself, i think i've done a quality job, I use direct burial wire in pipe, so it'll probably outlive me.

do you use a Tow-motor or a pick-up with 4 x 4 ?
Well Hi motor-T ! I am 'sleeving' pipe over wire here, the 'deer sling' allows my hands free to guide the wire into the pvc. There was absolutely not a single nick in this install, more than i can say for other cajun methods i have seen, including a van roof rack being torn off. I have been on crews that have the right equipment, and still seen conductor damage done.

Oh well!, guess i'll call the burn center, figured i'd get the heat for this thread. But hey, gimme some credit here, how many of you guys would attempt this alone?

now where's those done's pills????