|
1 members (Scott35),
261
guests, and
12
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Nov 2001
Posts: 6
OP
Junior Member
|
Is is acceptable (legal) to attach two wires to a single pole circuit breaker. I want both feeds on the same circuit. I just ran both wires back to the panel and attached both of them to the breaker.This is in Canada, but curious if its different in the US?
|
|
|
|
Joined: Oct 2000
Posts: 4,116 Likes: 4
Member
|
Dale,
The answer would depend on the breaker. Some are Listed for more than 1 wire, but most are not.
Bill
Bill
|
|
|
|
Joined: Oct 2000
Posts: 5,392
Member
|
Sq D QO is, other than that i dunno....
|
|
|
|
Joined: Mar 2001
Posts: 85
Member
|
Couldn't find anything on it in the CEC, I think Bills right about the breaker though. Any reason why you want to double them up?
|
|
|
|
Joined: Mar 2001
Posts: 2,056
Member
|
Why don't you just splice a pigtail?
|
|
|
|
Joined: Oct 2001
Posts: 81
Member
|
Curious on my part what part of Canada are you doing this?
|
|
|
|
Joined: Nov 2001
Posts: 6
OP
Junior Member
|
Full panel...went the route of an octogon box and 1 feed from the breaker
|
|
|
|
Joined: May 2001
Posts: 144
Moderator
|
There are code rules that this condition applies to.
In Ontario, Canada we (the Inspection Department) base our decision on the follwing code rules:
A maximum of one conductor per breaker is permitted unless the breaker is approved for terminating more than one conductor. - Rule 02-034
Section #2 states:
2-034 Use of Approved Equipment (see Appendix B) No one shall use any electrical equipment other than approved electrical equipment of a kind or type and rating approved for the specific purpose for which it is to be employed.
Appendix B states:
2-026 2-034 As a condition of approval of certain types of electrical equipment, the manufacturer supplies instructions pertaining to its installation. It is of the utmost importance that the installer closely follow installation instructions supplied by the manufacturer to fulfill the terms of the approval agreement.
Tony Moscioni Electrical Inspector © Electrical Safety Authority
|
|
|
Posts: 201
Joined: April 2004
|
|
|
|
|