#52114 05/19/05 02:58 PM
SJT Offline OP
We have a 225kva transformer, with 480v primary and 208 sec. The installation the way it is now, has 2 - 4" seal tights, each going to a 400amp switch. Are you allowed 2 diffrent disconnects on the secondary side? Do the secondary conductors have to terminate into a single switch or breaker? Such as a 600 amp main breaker panel? Can they end up into 2 switches?
Thanks
#52115 05/19/05 04:09 PM
Y
Is this in a Superivised Industrial site or not?? (240.2) definitions.If so read 240.90 if not read 240-21c.
#52116 05/20/05 02:57 PM
SJT Offline OP
Thanks for the input