Judge, depending on what code you're on-GFI's service recpt's are needed in any closet, crawl, attic, roof where the HVAC guy stuffed a furnace, or ac.
210.63 Heating, Air-Conditioning, and Refrigeration Equipment Outlet.
A 125-volt, single-phase, 15- or 20-ampere-rated receptacle outlet shall be installed at an accessible location for the servicing of heating, air-conditioning, and refrigeration equipment. The receptacle shall be located on the same level and within 7.5 m (25 ft) of the heating, air-conditioning, and refrigeration equipment. The receptacle outlet shall not be connected to the load side of the equipment disconnecting means.
FPN:See 210.8 for ground-fault circuit-interrupter requirements.
Section 210.63 is intended to prevent makeshift methods of obtaining 125-volt power for servicing and troubleshooting heating, air-conditioning, and refrigeration equipment. The reference to 210.8 in the fine print note to 210.63 reminds the Code user of the GFCI requirements for these receptacle outlets. The requirements in 210.52(E) for outdoor dwelling unit receptacles located within 25 ft of this equipment will meet the requirements of 210.63.
The requirements of 210.63 were expanded for the 2002 Code to improve worker safety. As a result, a receptacle outlet is now required for troubleshooting heating, air-conditioning, and refrigeration equipment at grade-accessible outdoor equipment and at rooftop units associated with one- and two-family dwelling units.
George, 210.52 as a 'section' covers recpt's in dwellings. And part 'A' is all the other rooms of a house, part 'B' is kitchens, pantry, dining rm., etc. Anyway, right before this section splits into these parts, you have this: And it covers all in the 'section'
210.52 Dwelling Unit Receptacle Outlets.
This section provides requirements for 125-volt, 15- and 20-ampere receptacle outlets. Receptacle outlets required by this section shall be in addition to any receptacle that is part of a luminaire (lighting fixture) or appliance, located within cabinets or cupboards, or located more than 1.7 m (51/2 ft) above the floor.
Then Part 'B' covers the two circuits required in 210.11(C)(1), and any from it that are part of the ones covered in part 'A', like walls in kitchen, pantry, breakfast room, dining room. And also the countertops they are intented for covered in part 'C'.
210.52B(1) Receptacle Outlets Served. In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit, the two or more 20-ampere small-appliance branch circuits required by 210.11(C)(1) shall serve all receptacle outlets covered by 210.52(A) and (C) and receptacle outlets for refrigeration equipment.
Then 210.52B(2)No other outlets
I believe in the 2005 code, it better defines the appliance garage issue. I'm not sure if it seperates them from these circuits too?
Either way, the appliance circuits rules apply to the DW/GB circuits, being "fastened in place". Another story all together.