1 members (Scott35), 102 guests, and 12 robots.
#51944 05/16/05 05:04 PM
home Offline OP
My two boys finished wiring a new house and said the AFCI breakers would not take a load. I checked the circuit with an anyliser and everthing checked out. I put a small load on the receptacle and the breaker tripped, I tried another AFCI breaker and the same thing. I put the load under a regular breaker and everything was fine. Both are Square D with one having a blue test button and one a green.My supplier says it's the circuit. Any comments?
#51945 05/16/05 05:22 PM
Check all your circuit *carefully*. Somewhere you have a ground touching a neutral.
#51946 05/16/05 05:50 PM
How many AF breakers will not hold 2? I would say the nutrals are crossed between the 2 tripping AF. Good luck.
#51947 05/16/05 11:34 PM
Yep, that sounds familiar, had the same problem one day when I was working on a live circuit and tripped the AFCI breaker when the ground and neutral touched. Sandro is right.
Good luck
Ron
#51948 05/18/05 11:03 PM
SquareD also had a recent AFCI recall. May or may not be related.
Larry Fine
Fine Electric Co.
fineelectricco.com
#51949 05/19/05 10:15 AM
Your boys know they can't use shared neutrals right?
#51950 05/19/05 01:12 PM
Larry, the SqD recall refers to AFCIs that don't trip when they should.
#51951 05/19/05 09:35 PM
As far as the recall goes the green buttons are new and not part of that. The blue buttons are the first sign of recalled breakers. Look at the date code stamped on the sticker just above the terminal. It should be in red. The affected codes are CN, DN, EN, FN, GN, HN, JN. These breakers have been recalled and should be replaced.
#51952 05/20/05 07:13 PM
Sugget you turn off power to circuit, disconnect the neutrals and ohm it out. If the neutral and ground are touching you should find it with an ohm meter. Good Luck
ed
#51953 06/09/05 09:12 AM
Home:
Did you ever get the problem figured out? If so what was it?
