ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 298 guests, and 11 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#51482 04/30/05 12:08 PM
Joined: Apr 2005
Posts: 3
J
Junior Member
I have been asked to reconnect a music Kill switch on a commercial Dj booth. Two single pole breakers have been tied together with a peg thru the throw handle on the breakers. One breaker controls dj booth power - the other is connected thru a normally open switch that connects to ground. ie: Close the switch breaker trips opening power breaker. This is a "reconnect" ~

#51483 04/30/05 12:36 PM
Joined: Nov 2003
Posts: 127
S
Member
I wouldn't want to be around when that switch fails...!


No wire bias here- I'm standing on neutral ground.
#51484 04/30/05 12:42 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
So what happens the day the breaker fails?

Sounds like with the existing wiring you could use a real shunt trip breaker.


Mark Heller
"Well - I oughta....." -Jackie Gleason
#51485 04/30/05 01:10 PM
Joined: Apr 2005
Posts: 3
J
Junior Member
I agree A Real Shunt breaker is needed.
Application wise is there anything that requires you not to do it. Breaker finds a ground - trips - Normal Operation ~

#51486 04/30/05 01:15 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Very bad idea in my opinion.

I also believe it would be a violation of 110.7

Quote
110.7 Insulation Integrity.
Completed wiring installations shall be free from short circuits and from grounds other than as required or permitted in Article 250.

It is very likely along with tripping the branch breaker you will trip a main putting people in the dark.

A handle tie will not always trip the other breaker, it is not intended to do that.

There are so many better ways to cut off a sound system. If I am not mistaken you can actually damage speakers by dropping the power out in the wrong order.

[This message has been edited by iwire (edited 04-30-2005).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#51487 04/30/05 01:24 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
iwire, good point there! Most sound equipment people I have worked with would have a heart attact if the amp fans were not allowed to run and cool the system before dropping power to it. Definately not good for the equipment either.


Mark Heller
"Well - I oughta....." -Jackie Gleason
#51488 04/30/05 01:26 PM
Joined: Apr 2005
Posts: 3
J
Junior Member
Thanks Fellows
I appreciate the Info...

#51489 05/01/05 12:23 AM
Joined: Feb 2005
Posts: 693
L
Member
I haven't thought out all of the ramifications, but how about using a GFCI instead, and using a pushbutton to connect the ground and neutral together.

Almost all GFCI will trip if the neutral is grounded, and there's no bolted-fault current strain on the equipment.


Larry Fine
Fine Electric Co.
fineelectricco.com
#51490 05/01/05 12:35 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Quote
how about using a GFCI instead, and using a pushbutton to connect the ground and neutral together.

This would violate 250.24(A)(5)

Quote
250.24(A)(5) Load-Side Grounding Connections. A grounding connection shall not be made to any grounded circuit conductor on the load side of the service disconnecting means except as otherwise permitted in this article.

How about running a switch leg, or use a contactor etc.

There is no need to short a breaker or trip a GFCI.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#51491 05/01/05 04:45 PM
Joined: Feb 2005
Posts: 693
L
Member
Oh, sure, bring doing it the right way into the conversation! lol


Larry Fine
Fine Electric Co.
fineelectricco.com

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5