Electricians revenge
0 members (), 171 guests, and 31 robots.
JFLS41 Offline OP
Help me to properly understand the 220.19 table for computing the demand factor for a 11KVa stove. Do you multiply 11,000 x 8 = 880 or do you figure it 8 x 1000 = 8,000? Not sure if I'm doing it right.
Thanks
Bob Offline
Read note 2 under the table. It explains the prodeedure.
JFLS41 Offline OP
I read that, still scratching my head... care to explain if you don't mind?
thanks
When using column C the math is already done. (1) 11kw range = 8kw, or 8 x 1000 as you said.
Roger
[This message has been edited by Roger (edited 04-26-2005).]