ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 477 guests, and 12 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
#51008 04/18/05 06:45 PM
Joined: Mar 2002
Posts: 179
D
derater Offline OP
Member
Dropped off 100a panel and some 3/0 on a spool at a friends.He's a mechanic, this project is a trade deal.In the mean time
he rented adjacent(8')steel building out and someone ran 2/0 2-wire and powered the
panel.What now? Ground rod and structure?
and/or separate ground conductor back to main.And please explain the ground potential
and other hazards with this install.

#51009 04/18/05 07:21 PM
Joined: Jan 2001
Posts: 1,044
Tom Offline
Member
I swear, some people should just keep their hands in their pockets at all times & resist the urge to do electrical work.


I'm e-mailing you a handout on subpanels in separate buildings. It should cover what you need to know about grounding & bonding with the exception of the required bonding to the structural steel.

Tom


Few things are harder to put up with than the annoyance of a good example.
#51010 04/18/05 07:49 PM
Joined: Jan 2005
Posts: 5,445
Likes: 3
Cat Servant
Member
Now Tom, be nice....this is one area where the code stumbles around some. Why, just a few months back, the IAEI ((inspectors' org) asked three experts, and came up with four answers!

The article was in the Nov/Dec2003 issue of IAEA news, was called "# Chiefs come full circle on parallel paths and end on a tangent," and you should be able to read it at IAEI.org.

For a very simple summary of MY view....
The ground rod is for lightning protection. Every building gets one.
The service is where the neutral and ground get separated...and stay separated. Every panel downstream get a ground wire sized to the current- and the ground rod at the other building gets bonded to this at the panel.
And...I don't care how balanced your loads are, or if there is only 240v. equipment in that other building....run a neutral to the panel. If in any doubt, it never hurts ti size it to the service the panel provides.

Two wires? Sure- if he only wants 120v.

#51011 04/19/05 06:39 PM
Joined: Mar 2002
Posts: 179
D
derater Offline OP
Member
Well it is a 2 wire w/ noodle, but no ground.

#51012 04/19/05 07:18 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
OK thought about it, and theres something wrong here....

TWO WIRE PANEL?! Hot (1), neutral (1), thats it?

Fed with 2/0, or 3/0? Either way, next question is... how is the other side of the panel fed? Double lugged? From a 100A single pole breaker? One phase dead? Or is the only time I'll hear about a 120 only panel?

What will it take to get the other two conductors there.

Anyway, steel structure, no ground! With no fault path, a short circuit could kill someone coming out of the rain, and locking their hand around an energized door knob. Forget anything in regaurds to lightning, although also a hazard, it is more remote than the chances of other (in this case likely) electricution hazards. Like.... an HID, or flouresant fixture imposing 300-1200 volts on the metal surfaces of the building. Or, if someone, and it is likely here, that the nuetral is bonded to the panel can by the stupid screw that comes with them, that it is a parralel path for neutral current. A few minutes with a calculator with known loads, and I could give you an rough estimated amperage of a bare foot hippy leaning against the wall. (No offense to hippies who wear shoes.....)

If this is in conduit, yank out the the 2/0, or 3/0, and give it a #2 THHN feed, with 3-wires and a #6 ground. Or the other method described in 250.32 (Ground rod, neutral bond, AND bond the steel.) Depending if there is a metalic path between this shock chamber, and the main building.

www.markhellerelectric.com/250.32.pdf

[This message has been edited by e57 (edited 04-19-2005).]


Mark Heller
"Well - I oughta....." -Jackie Gleason
#51013 04/19/05 08:06 PM
Joined: Mar 2002
Posts: 179
D
derater Offline OP
Member
Sorry if I wasn't clear- it is 2 ungrounded
and 1 grounded-but no GROUNDING wire.

#51014 04/19/05 08:24 PM
Joined: Oct 2004
Posts: 135
B
Member
Well that's alot different. I'm not clear what it is you're doing though. Are you rewiring the building that's fed with a 3 wire feeder? 2 hots and a grounded conductor. Is it conduit or cable?

[This message has been edited by BobH (edited 04-19-2005).]

#51015 04/19/05 09:05 PM
Joined: Jan 2005
Posts: 5,445
Likes: 3
Cat Servant
Member
"Thinking outside of the code" here....no ground....feed the damn place through a GFI breaker?

#51016 04/19/05 09:15 PM
Joined: Mar 2002
Posts: 179
D
derater Offline OP
Member
Obviously I need to work on my communication skills.My understanding is sub-panels require 3-wire w/ground.In as much as the 2nd blg.is only 8' from the blg. w/ main panel (that feeds the sub),
and it's steel(2nd. blg.).My concern is shock hazard.I
wouldn't want to see my friend have legal problems and a clear explanation of what and why of what needs added (gnd. wire?)I had left the stuff there to do it right myself but someone jumped the gun.

#51017 04/19/05 09:18 PM
Joined: Feb 2003
Posts: 939
F
Member
let me ask this to make sure i understood this question.

is the building is a rental unit like rent a storage space or rent a garage ??

if this is a rental building it should have a electricican deal with this because the code is pretty strict with this and also is any water pipe or telephone wire there ??

if so you have to run full 4 wire set up.

Merci, Marc

P.S. make sure that building well gfci'ed


Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)

Page 1 of 2 1 2

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5