|
1 members (CoolWill),
250
guests, and
13
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Mar 2004
Posts: 814
OP
Member
|
On a resi rough in should the breakers be terminated before inspection, or just the grounding and neutral conductors? I don't like the idea of the breakers being terminated in a hot panel with no devices installed yet.
|
|
|
|
Joined: Mar 2005
Posts: 212
Member
|
When I did houses in California we never set circuit breakers until we did the trim. Here in Idaho it's standard to install them at rough in, but there isn't a meter set until the final inspection so nothing is hot. Sometimes a meter is set earlier if a house needs heat etc. Since I don't do houses anymore I'm not sure how this is handled. I'm never comfortable with a situation where others can energize circuits that may not be clear.
|
|
|
|
Joined: Sep 2004
Posts: 167
Member
|
Theft is a big problem here so we let it go until final.
Larry LeVoir Inspector City of Irvine, CA
|
|
|
|
Joined: Aug 2001
Posts: 335
Member
|
Around here the only things the inspector looks at during rough in are the ground path, neutral path and installation of the materials in the walls & ceilings. If all this is ok and I've put breakers in a (dead) panel they just ignore them. If the panel is hot he's gonna be "a tad" disturbed. Sandsnow has the real point ... wanna buy them twice?
|
|
|
|
Joined: Jul 2004
Posts: 9,923 Likes: 32
Member
|
In SW Fla the panel and meter get set at the service rough and they fire it up with 1 GFCI breaker and the garage receptacle right after the roof is black. The rest of the breakers get put in with the trim, close to the end.
Greg Fretwell
|
|
|
|
Joined: May 2003
Posts: 74
Member
|
The purpose of a rough inspection is to check the work that will be concealed.
|
|
|
|
Joined: Feb 2002
Posts: 2,233
Member
|
I would not expect the breakers to be installed on the rough inspection. I would expect maybe 1 or 2 breakers for a service inspection to get some temp power in a construction site, but the rest of the breakers I would see them on the final inspection. You don't want the painters to get slop all over the breakers no would we.
|
|
|
|
Joined: Mar 2004
Posts: 814
OP
Member
|
Thanks guys. hey Harold no worry about paint on the breakers here in Arizona they're always outside!
|
|
|
|
Joined: Apr 2001
Posts: 449
Member
|
Another reason not to install and terminate all of the branch CBs at time of rough-in is safety. Do you really want anyone on the job to be able to switch on a CB and heat up a circuit with nothing terminated on the other end? Sounds like a good way to get a painter zapped!
|
|
|
|
Joined: Apr 2004
Posts: 20
Member
|
We label the home runs and leave them tied up neatly (next to the panel, NOT terminated) so the inspector can look at what will be terminated. The only thing I terminate is the receptacle that is next to the panel.
|
|
|
Posts: 201
Joined: April 2004
|
|
|
|
|