JakeJ1 Offline OP
Is there an allowance for a splice (inside a junction box) for a "Feeder Cable". The NEC doesn't seem to mention it one way or the other.
#50168 04/01/05 05:06 PM
You are right, NEC doesn't say restriction for this, at least, I couldn't find it.
According to 110.14 (B), 215 and 300.13. But be carefull, some utility companies don't permit to do that before meters to avoid stealing energy.
#50169 04/01/05 05:53 PM
It would be very unusual for a power company to be concerned with feeders.
They concern themselves with service conductors.
The NEC does not prohibit splices in either.
#50170 04/01/05 06:24 PM
Power utilitys also arent required to follow the NEC. They are governed by I believe the NESC(national electric suppliers code?)