ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 121 guests, and 10 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Mar 2005
Posts: 16
J
JoeMed Offline OP
Member
This installation has each phase double lugged to avoid double tapping the main service feeder breaker. From the service pedestal there is a 200amp service disconnect that feeds two 100amp panels, each is fed with 2/0 THHN (yes, a tad under) and both the 2/0 are lugged together one slightly longer to accommodate the breaker. To finish the installation, each of the wires go to a separate 100amp main breaker in a 100amp panel. Please advise was this an acceptable solution to this installation? Not my install. I have not seen this before.

Joined: Dec 2003
Posts: 524
Member
...Generally,(2)wires under one lug is a violation,unless that lug/breaker is listed for such..as far as I know,Square D,are the only breakers whose lugs are listed for (2)wires,..but 2/0?? how did they fit (2) of them under(1)lug?? sounds fishy to me...Good Luck!!
Russ

[This message has been edited by Attic Rat (edited 03-24-2005).]


.."if it ain't fixed,don't break it...call a Licensed Electrician"
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
I am not aware of any "box" lug (the ones with a hole in them) that is rated for multiple conductors per hole. Lugs with "pressure pads" are often rated for two conductors.

Joined: Jan 2005
Posts: 5,445
Likes: 3
Cat Servant
Member
Any electrical supply house has, or can get, a variety of devices to make this sort of connection properly.
One type has openings for three wires.....use with a short pigtail from the breaker.
The other is a machined block with connections for two wires, and a solid 'tail' that is inserted into the breaker.

Joined: Mar 2005
Posts: 16
J
JoeMed Offline OP
Member
thank you for the responses, I was n to clear on the lug. It is a double lug, with one wire in each lug, one wire longer to accommodate the breaker. Sound like it is not as bad as I thought?


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5