1 members (Scott35), 523 guests, and 33 robots.
cgw Offline OP
Does any one have problems with running NM cable in small commercial wood frame buildings (say a apartment complex office/community center (less than 100 people)) as opposed to MC cable?
Is the cost savings (material and labor) significant?
How many stories?
I might be wrong,but I thought Romex was not allowed in any commercial building.
Is a condominium or apartment complex above three stories considered commercial or residential?
Edward
Thanks
Edward
cgw Offline OP
One story, type V (wood frame) construction.
Based on your information, it's not an NEC issue.
Personally, I (as an EC) do not put MNC in comm buildings. But, remember, this is my personal choice.
cgw
In the county I live in its acceptable to run romex in a comm bldg but I refuse to do it. Are apt complex's concidered comm work in your area?
Rob
we just wired up a one story medical building. we ran romex for the offices, kitchen, reception, and waiting rooms; and BX for the examination rooms...if there wern't any examination rooms, i am positive my boss would have ran all romex(speed/cost of running the wire, ect.)if it's not over 3 stories then go for it...just don't run it in open runs above a drop ceiling.
for a complete list of where you are allowed to use NM cable, look at
Article 334.10--Uses Permitted.
for complete list of where you can't use it look at Article 334.12--Uses Not Permitted
e57 Offline
Depends on your local codes for fire ratings, I'd check your Inspector before you start.
I don't have a problem using NM in any wood frame construction.
BTW, the 3 story limit was removed in the 2002 book.
what is (excessive) moisture or dampness?
in 334.12 (10) (d)
is a pole barn a hazardous location?
because of hay or grain dust maybe.
could I use NM in the pole barn?
