|
0 members (),
205
guests, and
28
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Oct 2004
Posts: 72
OP
Member
|
250.30 (4) "the grounding electrode shall be as near as practicable to and preferably in the same area as the grounding electrode conductor connection to the system."
SYSTEM, are they talken electrical system or grounding system? I like to drive rods at whare the water enters the house because thats what your backing up any way the water pipe and you got to pull the grounding electrode conductor their any way so why not just keep goen another 15' or so and hit a couple rods right
|
|
|
|
Joined: Jan 2002
Posts: 1,457
Member
|
So what is the question? SYSTEM, are they talken electrical system or grounding system? I like to drive rods at whare the water enters the house because thats what your backing up any way the water pipe and you got to pull the grounding electrode conductor their any way so why not just keep goen another 15' or so and hit a couple rods right Or are you entering the worlds longest sentence contest?
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
250.30 rarely applies to dwelling unit installations. It applies to separately serived systems(SDS) and the grounding electrode for the SDS should be as close as possible to the SDS. Don
Don(resqcapt19)
|
|
|
|
Joined: Oct 2004
Posts: 72
OP
Member
|
Ya that sentince took the gold. and i should be looken closer at the article titles befor i just start readen any old thing.
So the Question was really about whare to put the ground rods. Is one place beter then a nother?
|
|
|
|
Joined: Jan 2003
Posts: 1,429
Member
|
Quote: "I like to drive rods at whare the water enters the house" __________________________________________
I hope you have the area marked out before you drive your rods, we try to keep our distance from utility lines, here in New Jersey if we dig or drive ground rods, we have to notify the utility dig service, or the fines can be stiff.
[This message has been edited by LK (edited 02-21-2005).]
|
|
|
|
Joined: Jan 2005
Posts: 40
Member
|
Ok lets say You do drive them next to the water main then for some reason in a couple of years [water line break] Idot on backhoe has no clue ground rods are there in my opinon keep them next to the servie drop.....
|
|
|
|
Joined: Feb 2002
Posts: 2,233
Member
|
I try to look for anything underground before I drive the ground rods. Like sewer pipes, oil/gas lines, downspouts, etc. As LV said, here in NJ we also are suppose to call for a mark out of utility lines before we dig anything. A friend of mine drove a rod right through the neighbors waste pipe. Had to dig up pipe, and fix pipe. Lost all profit on that job.
|
|
|
|
Joined: Jan 2002
Posts: 1,457
Member
|
A friend of mine drove a rod right through the neighbors waste pipe That stinks.
|
|
|
Posts: 44
Joined: July 2013
|
|
|
|
|