1 members (Scott35), 552 guests, and 38 robots.
#48632 02/16/05 08:27 PM
ToHo Offline OP
I got a call from a customer to replace his OH service.The meter is located on a pole out by the street.The existing service is carried to the house on a messenger cable.The service then gets spliced to a SEU to enter the house.My question is about the type of insulation on the conductors used w/ the messenger cable to bring the service to house.I'm looking at table 310.20. I'd like to know if there is one type (THHN,XHHW etc.)that is used more often than others. Also the Temp rating of 75 or 90.Any info is greatly appreciated....Thanks ToHo
#48633 02/16/05 08:48 PM
Bob Offline
This site has your information.
http://www.sural.com/products/insulated/drop.htm
#48634 02/17/05 03:10 PM
Are you sure it is the customers cable to replace?
It may be the power companies cable.
#48635 02/17/05 03:48 PM
ToHo Offline OP