Is this paper insulated lead covered 3 conductor cable in a duct bank? Why change. If you don't break the lead cover, it will last 300 years.
In a duct bank, 1 cable per duct
100% LF amps = 505
75% LF amps = 550
50% LF amps = 581.
If you have more that one cable in the ducts bank the rating drops. You probably need to contact a MFG to get the rating.
[This message has been edited by Bob (edited 02-16-2005).]