Safety at heights?
0 members (), 181 guests, and 10 robots.
BillK Offline OP
Has anybody heard anything about new codes reguarding 3" hubs to a residential load center? Anybody have details???
Have heard it might be for panels 400A and up.
Bill K
Hi Bill,
I have not heard anything.
310.15(B)(6) allows 400 KCMIL THWN copper for a 400 amp dwelling service.
You could go traditional and use 500 KCMIL THWN, both fit in 2 1/2 per Annex C - Table C1 EMT and C4 IMC. In table C8 for RMC, 500 KCMIL would have to be in 3 inch.
Bill:
Welcome to the forums.....
Could you be refering to a utility (POCO) requirement???
Here in NJ (PSE&G) a 'mast' service requires a 2 1/2" RGC minimum.