by NORCAL - 03/19/24 05:11 PM
0 members (), 260 guests, and 19 robots.
#48292 02/08/05 01:18 PM
V
velect Offline OP
Is there a dimmer that would control a combination of 2 incandescent recessed cans and a set of cable lights with a magnetic transformer
#48293 02/08/05 03:58 PM
A magnetic LV dimmer will do the job. They are OK for Magnetic LV and standard Incandescent. If I remember right, they block DC current that would otherwise heat up the magnetic transformer primary.
Lutron should have what you are looking for.
#48294 02/10/05 12:33 PM
V
velect Offline OP
Don't the low voltage dimmers from Lutron require a neutral. There is no neutral at either three way location
#48295 02/10/05 03:00 PM
Neutral is required for "Electronic" lv dimmers not magnetic