Customer has 200amp OH service w/ 2 100amp meters(double gang meter) feeding 2 100amp panels w/100amp main breakers.Customer wants one panel to be up graded to a 200amp.So the end result would be a 200amp & 100amp panel. I would think I would have to upgrade to a 2 gang 200amp meter box.The house has gas heat and appliances. The load calculation on the house isnt changing by a large amount. Just needs more breaker space for attic renovation.That said ... the 200amp OH service should be ok.. any input is greatly appreciated..ToHo
|
|
|
|
Joined: Sep 2004
Posts: 86
Member
|
You would have to upgrade to the two 200 amp meter sockets. Sounds like a lot of work if the loads aren't changing. How about installing a 30 circuit 100 amp main breaker panel and upgrading the grounding? SQD makes one and I believe Cutler Hammer does to. Ron
|
|
|
|
Joined: Dec 2004
Posts: 46
OP
Member
|
customer wants the 200amp panel for future use if necessary. I don't believe The utility Co. rates the residential service as a continuous load?(only commercial) I'm not sure at what point the utility Co. would want me to upgrade the 200amp OH service. ToHo
|
|
|
|
Joined: Nov 2002
Posts: 267
Member
|
You may want to consider the Milbank number U2601-XL. It's a 2-gang horozontal one 100 amp and one 200 amp. Now you can have a 200 amp main 40 ckt on one side and a 100 amp 30 ckt on the other. They're mostly used where there's one larger sq ft home next to a smaller apt/in law.
|
|
|
|
Joined: Dec 2004
Posts: 46
OP
Member
|
wirenutt.. thanks..I did not know milbank made a combo meter enclosure like that.. I just have to check with the poco to see if 4/0 seu service riser will be large enough for both services.. Thanks again ToHo
|
|
|
|
Joined: Sep 2004
Posts: 86
Member
|
Hey Wirenutt, 35 years in the business and thats the first time I've heard Milbank had such a meter socket. Very interesting. Will have to see if WE energies approval is on that one for future use. Education never comes to an end. Ron
|
|
|
|
Joined: Nov 2002
Posts: 267
Member
|
I didn't know it was made til I had started working in a supply house. After years in the field now have acsess to all this info., figures, LOL....
|
|
|
Posts: 70
Joined: January 2002
|
|
|
|
|