#46405 12/21/04 11:43 PM
Joined: Aug 2001
Posts: 7,520
P
pauluk Offline OP
Member
Seems there might be a few things to criticize here:
http://www.dulley.com/diy/dw107.htm

Joined: Aug 2001
Posts: 335
S
Member
Don't ya just love it?

Joined: Nov 2003
Posts: 269
E
Member
Quote
The National Electrical Code now requires No. 12 gauge wire for all residential electrical wiring.
Huh? [Linked Image] [Linked Image]


John
Joined: Jan 2004
Posts: 66
C
Member
Quote
The National Electrical Code now requires No. 12 gauge wire for all residential electrical wiring.

wow, it good i read that link. i had origionally thought that the wire size is dependant on the breaker size. now i am more educated and know that the NEC requires No. 12 on all circuits. today i ripped out the 8 gauge going to my stove and the 10 gauge going to my dryer and replaced them with 12 gauge. tomorrow im going to go buy some more 12 gauge to replace that dangerously oversized feeder going to the 100 amp subpanel in my garage

[Linked Image]

Joined: Nov 2003
Posts: 127
S
Member
Quote
Outdoor wiring projects are not difficult for a do-it-yourselfer, but, for safety reasons, outdoor wiring codes must be followed.
I was unaware of the NEC Outdoor Code- it would make much more sense to incorporate it in the standard NEC [Linked Image]

No mention of load evaluation in the circuit to be extended, either- Grrrr!!!!!!


No wire bias here- I'm standing on neutral ground.
Joined: Apr 2002
Posts: 914
E
Member
Quote
Dig the trench. If you are using EMT conduit or UF cable, the trench should be 12 inches deep. Rigid metal or plastic conduit requires a 6-inch depth

This must be the question I missed on my license exam. I thought that in most circumstances UF needed to 24" deep in a yard unless covered with 2" of concrete. I didn't even know you could bury EMT and I thought rigid needed to be 18". I guess you learn something every day.

Joined: Jul 2004
Posts: 625
S
Member
RMC only needs 6" except underneath things like driveways, parking areas (that's "car parks" to you, Paul [Linked Image] ), and runways.

Joined: Nov 2003
Posts: 127
S
Member
How deep should the trench be to bury the rotten advice of some of those DYI (Do-Yourself-In) websites??? I won't mention the six-foot rule for the webmasters of those sites hehehe...


No wire bias here- I'm standing on neutral ground.
Joined: Aug 2001
Posts: 7,520
P
pauluk Offline OP
Member
Aw, shoot! You mean I shouldn't rely on that site as an educatiuonal resource for American outdoor wiring practices? [Linked Image]

The #12 for all circuits is the first thing that caught my attention there.

Joined: Dec 2000
Posts: 4,294
Member
The author's e-mail info is:

contact@dulley.com

To publish irresponsible information like this while posing as an "expert"?.

Eagle [Linked Image]
Quote
I didn't even know you could bury EMT


[Linked Image]

This was actually inside a building where the penetration went outside. The rest was indistinguishable as conduit.



[This message has been edited by electure (edited 12-24-2004).]