ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 218 guests, and 27 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
#46288 12/18/04 11:27 AM
Joined: Mar 2002
Posts: 125
S
Member
Has anyone installed a 208 to 40 buck boost. I intalled a Ge the wiring said to attach the line side to the h1 and h2 and line to x1 and x2 and wire nut x2 and x3. Well the trans smoked. does the config seem right. Thanks

#46289 12/18/04 06:29 PM
Joined: Apr 2002
Posts: 2,527
B
Moderator
 
See www.federalpacific.com/literature/drytrans/FPTS-RTB-0701.pdf possibly “figure B” on page 40.. There are plenty of variations—judge for yourself.

#46290 12/18/04 10:38 PM
Joined: Mar 2002
Posts: 125
S
Member
The trans I had only had a H! and H2. Do these get tied to line or load. It is like pg 42 diagram 2

#46291 12/18/04 11:38 PM
Joined: Jan 2003
Posts: 33
C
Member
Your connections do not sound correct, can you post the xfmr data or connection information that was supplied? Perhaps we can decipher better then.

#46292 12/19/04 09:43 AM
Joined: Oct 2000
Posts: 2,723
Likes: 1
Broom Pusher and
Member
Looks like you have a 240 VAC × 16/32 VAC Split Coil (Secondary) 1Ø Isolated Transformer - judging from the Voltages listed and the Terminals
(Input = 208 VAC, Output = 240 VAC - hence the 32 VAC Secondary, + H1, H2, X1, X2, X3, X4).

Take a look at these Schematics from the Technical Reference Section:

[Linked Image]
Image #1: Pictorial View

[Linked Image]
Image #2: 1 Line View

Actually, the Voltages listed in these Schematics differ from yours, but the concepts are the same.
Along with this, instead of having a Split Coil Primary, or a Primary setup for use at either 120 or 240 VAC as these drawings show, your Transformer has a Single Primary Coil wound for 240 VAC (or 208 VAC).

The Terminals on your Xformer would be "H1" and "H2" only, so in this case, your Transformer would have the "H2" Termination done to where the "H4" Termination is shown in the Schematics.
This way, the Secondary Coils are in a Series Adding Connection methodology...

FYI, refer to the Tech. Reference section for more drawings and details, regarding the Voltage Boosting and Voltage Bucking setups.

Let us know if you do not understand this information, and if the Transformer is salvagable,
or you are able to Put The Smoke Back Inside The Windings
[Linked Image]

Scott35


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
#46293 12/19/04 10:34 AM
Joined: Mar 2002
Posts: 125
S
Member
I do not have the specs. I ws talking to a friend and he said the ame thing about not sounding right. When I get the newone monday I will try to post them. thanks for the help.

#46294 12/19/04 11:43 AM
Joined: Jun 2004
Posts: 206
C
Member
Sparks, take a look at page 44 diagram 10A. It looks more like what you are trying to do.
Al

#46295 12/19/04 01:28 PM
Joined: Mar 2002
Posts: 125
S
Member
I tied H1 to 1leg of input208 and H2 to other leg of input. Then wire nuted the x2-x3 together. Then 1leg of output to x1 and the other leg to x2.

#46296 12/19/04 05:03 PM
Joined: Oct 2004
Posts: 806
Member
Sparks; from what you just posted sounds ilke you've connected the primary correctly, but the x2/x3 connection shorted half of the secondary winding. The connection from primary to secondary as in the diagrams was missing from your hookup. So:

Wire H1 to one leg of 208;
Nut H2 AND x1 together, this is the other leg of 208;
Cap off x2; not used here
LOAD will connect as :
One leg to H1;
Other leg to x3

That should do it. Comments, gentlemen?


Stupid should be painful.
#46297 12/19/04 05:43 PM
Joined: Mar 2002
Posts: 125
S
Member
That sound more like it. The trans came out of the box with no paperwork, so I had to go with what was on the trans itself. everyone thanks for the help. I'll try not to smoke onother one.

Page 1 of 2 1 2

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5