by ale348 - 03/29/24 01:09 AM
by NORCAL - 03/19/24 05:11 PM
#46267 12/17/04 09:46 PM
Do you typically install a GFCI for a garbage disposal receptacle?
#46268 12/17/04 09:55 PM
Normally you don't GFCI protect fixed appliances. Roof De-ice being an exception. Just to let you know I have had inspectors make me install a single receptacle for the disposal so nothing else can be plugged in down there.
#46269 12/17/04 09:55 PM
I typically wire directly to them without a cord and plug, or receptacle.
Dave
#46270 12/17/04 10:52 PM
There is a single recep, under the kitchen sink in our home, that is fed by a 15A multi-wire circuit. One half of the recep is switched, and supplies the disposer. The other recep supplies the dishwasher. Of course the recep is supplied by a 2-pole breaker.
Northbayec - I read 210.8(A)(3)Exception and the NEC Handbook commentary in 426.28. The second to last paragraph in the commentary says, "It is important to understand that this required equipment protection is not the same as a ground-fault circuit interrupter used for personal protection that trips at 5 milliampteres (+/-1 milliampere)." Is the equipment the NEC is not referring to, the standard GFCI receps referred to in 210.8?
#46271 12/18/04 01:04 AM
F
No GFCI for disposals around here (western Pa), countertop recpts only in the kitchen.
Typically hard wired as are the dishwashers. The exception being tract houses which we install a switched standard duplex 15amp recpt on it's own 20a circuit in the sink base for the disposal. Another one unswitched on the wall behind the dishwasher also on it's own 20a circuit. No GFCI in either case.
Frank
#46272 12/18/04 05:46 AM
Question:
Do you have to install a wall switch for the dishwasher in a one family dwelling if it is hard wired?
PS: The term "kitchen waste disposers" is used in the NEC because some people thought that all "garbage" was to be put into the sink!
#46273 12/18/04 07:30 AM
No. [Linked Image]
Does the dishwasher have a switch 'marked off'?
Is the electric panel in sight?
Bob
#46274 12/18/04 07:37 AM
Electric Ian
Are you asking if it is required?
Depends, commercial kitchen or dwelling unit kitchen?
In a dwelling unit kitchen only 15 and 20 amp receptacles that serve counter tops must be GFCI protected.
So a disposal outlet under the counter is not required to be GFCI protected.
In a commercial kitchen if you did have a cord connected disposal connected to any 15 or 20 amp 120 volt receptacles it would be required to be GFCI protected.
ALL 15 & 20 amp 120 volt receptacles in commercial kitchens must have GFCI protections...no exceptions.
Bob
#46275 12/18/04 08:26 AM
V
My local inspector requires breaker lockouts on hardwired dishwashers. Also on harwired built-in ovens, cooktops and saunas
#46276 12/18/04 11:13 AM
iwire
No, I know it is not required but I was wondering if any of you guys typically install one. What sparked my curiousity on this subject was an online installation manual for a particular brand disposal (forget which one off hand) that "recommended" connection to a GFCI receptacle. I thought, hmm, that's interesting cause I've never done so and was just wondering if others do. Keep in mind the manufacturer usd the term "recommend" not "required".
