1 members (Scott35), 524 guests, and 23 robots.
#45074 11/18/04 08:31 PM
I need to install a rotary phase converter tomarrow and haven't had time to research as much as I had wanted. If anyone can help it would be greatly appreciated.
Here are the specs:
Runs 220V three phase equipment (In this case an ice cream maker) from a 220v single phase source. The motor is 3 H.P. I'll be installing it approx 30ft from main panel to a 3 phased disconnect then to the phase converter.
My question is what size wire should I use for the branch circuit conductors and what size breaker at the panel? I had already run #12 Romex assuming a single phase 220v load protected by a 2-pole 20. However, the customer got a good deal on a 3 phase ice cream maker. I'm not sure if #12 will still be OK.
Again, any comments would be greatly appreciated.
Ron Offline
You will have to identify what the nameplate states for minimum circuit amps, and max breaker size, then work from there. If it says #12 is ok, then it's ok. It will probably have a 30 or 35A max breaker size.