An inspector told me I could not reduce the size of conduit in a run except at the termination. The contractor ran a 2" PVC underground. At grade level I installed a Female Adaptor and a 2"x1" reducing bushing. I then ran 1" sealtight to a small panel in a piece of equipment. The circuit was 3 #8, 1#10 Grd. The total length of the entire run was only about 12'. He said "It's somewhere in the code book". Can someone save me a hassle and let me know where to find that one? Thanks
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
The inspector can not find it because that rule does not exist.
While most times it is not a great idea it is not a code violation.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Nov 2002
Posts: 244
OP
Member
|
I agree. I have never run across that rule either. By the way, that was the same inspector I mentioned in another thread I started a while back. "Inspectors who are #+%*&".
|
|
|
|
Joined: Aug 2001
Posts: 335
Member
|
Try my classic response: "Thanks for pointing that out. When you get back to the office would you call me and tell me the code section so I can read up on it. I'd hate to get caught in the same mistake twice."
It usually works; plus he's at the other end of the phone now and it's easier for him to say he'll let it go when he's not face to face.
|
|
|
|
Joined: Jun 2003
Posts: 1,143
Member
|
As others have said - he's talking out of his errr, pants...
As long as your within limits for conductor fill (which you are) there's nothing in th Code that prohibits it.
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
Tell the inspector he/she is looking from the wrong end, and that in reallity, you increased the conduit size and did not reduce it. I know, and I apologize. Roger
|
|
|
|
Joined: Nov 2002
Posts: 244
OP
Member
|
I just got back from an out of town job (3 days). I got called on one thing. No plastic bushings on 3" PVC Terminal adaptors. The contractor oversized the underground conduit from plan specs from 2" to 3". The pull was 2 #1 and 1#8 Grd. So as you can can imagine there are three dinkey little wires coming out of a huge conduit, not even touching the edges. The inspector made me tear everything apart to install bushings. I believe in bell ends for feeding but do you always use bushings on PVC and is this a fair call?
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
I rarely use PVC/RNC, and dare I say don't often use bushings on it either, because often the only times I use it, it will have Bell End, and a steel conduit on the other. But yep, required.
352.46 Bushings. Where a conduit enters a box, fitting, or other enclosure, a bushing or adapter shall be provided to protect the wire from abrasion unless the box, fitting, or enclosure design provides equivalent protection.
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|