Trekkie76;
thanks for the enlightenment guys. I have to try and unlearn what I thought I knew
Having done that several hundred times throughout my Career, it's completely understandable. Thankfully, we all now have resources - like ECN, to not only get the correct answers/theories/information, but to find out just what we need to learn!
Every time I log-in to ECN, I learn at least 10 new things, and alter another 10 previously thought things!
Now to the system Grounding thingee:
A couple things which may assist in grasping the whole idea of just why a certain Conductor's connection to Earth does not really effect the performance of
Normal Operations Of Equipment (excluding the problems of High Voltage stresses to Insulation and such) are as follows:
1: A 1Ø 3 Wire system - voltage = 120/240 VAC, where the Center Tapped "Neutral" Conductor is
NOT connected to the Earth at the Transformer or the Service, but the Metallic Equipment and any Equipment Grounding Conductors are "Bonded" to the Neutral Conductor, at the Service Equipment only.
Everything is the same as normal, only no physical type electrical connection is done to the Earth Ground (the system is not "Earthed").
A Fault from either one of the "Line" Conductors - the ones which would normally be the "Ungrounded Conductors" (Secondary Coil's ends, not the Center Tap), to the Metallic Panelboard's Enclosure, will react exactly the same as if the Fault (Short Circuit) occured directly between Circuit Conductors (Line to Neutral or Line to Line).
The Current will flow from the source and back to the source, via the Circuit Conductors.
Connect the above system to the Earth - thereby Earth Grounding it at the Transformer and the Service, and still the same thing happens.
A very small amount of Current will flow between the Service and the Transformer via the Earth. The level of Current will be dependent on the total Impedance between these two points.
Also, the small amount of Current flowing through the Earth doesn't only happen during a Ground Fault scenario. It is natural for Current to flow during normal operations through the Earth, and across commonly connected electrodes to other Services (City Cold Water piping, connected to multiple Services as Grounding Electrode Systems).
The levels in the C.W. pipes may be much higher than levels flowing through the Earth Ground to the Transformer.
This will become very evident when studying Kirchoff's Laws, and is one of the reasons for Roger's suggestion as to the study of Kirchoff's Laws of Current and Voltage.
2:Using the same 1Ø 3 Wire Transformer and Service, instead of Bonding the Center Tapped Neutral Conductor to Earth, - call it "X0", let's instead bond the "Left-Hand Secondary Coil End" - call it "X1", to Earth at both the Transformer and the Service(s).
Again, the entire system and connected Equipment will operate properly - even with a Ground Fault.
Only thing different now is the highest Voltage to Ground will be 240 Volts, instead of only 120 Volts with a Grounded Center Tap Neutral.
The Voltage to Ground will be either 120 VAC (from the Center Tap Neutral to Earth Ground or Grounded Metallic Equipment/EGCs), or 240 VAC (From Terminal "X2" to Earth Ground or Grounded Metallic Equipment/EGCs).
Voltage to Ground on "X1" will be Zero (close to Zero at the Service, becoming higher as the distance of circuitry runs increases).
As you can see here, the overall operation is not very dependent on Earthing, in order for things to operate.
Just wanted to add my 2¢
Scott35