#438 01/20/01 04:23 AM
Joined: Jan 2001
Posts: 1
T
TP2150 Offline OP
Junior Member
I am putting in a small laundry room in my garage. I have an electrical plug in the room currently active. I ran electricity from it to another outlet then though a wall switch connected to a single bulb ceiling light. The new and old outlets work great, though when I turn on the overhead light the 30 AMP fuse blows. I had nothing plugged into the outlets at this time. Any suggestions as to why the light is blowing the fuse.

Thanks

#439 01/20/01 07:12 AM
Joined: Oct 2000
Posts: 5,392
S
Member
if the switch blows the fuse, then it's probably wired hot to neutral, creating a "dead short". Also, If you are on a 30 A fuse for this, it's not to code.