Hi, anybody ever had any experience with Arc fault breakers on HID ckts?
Is there any problem using these on an HID ckt.
thanks
mustang
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
Not yet, but it is something I would worry about. Maybe temp up a few just to find out, let us know how it goes. I think the cap discharge may pop it.
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
Joined: Feb 2004
Posts: 494
OP
Member
|
i know of a company who is specifying these in all of their panels. shared neutrals is a problem with AFCI's and lightning, freq, and shock.
-regards
mustang
|
|
|
|
Joined: Feb 2003
Posts: 939
Member
|
the other thing i am little condersing about AFCI if run with HID lighting circuit the concats inside the breaker may not handle the surge or inrushing current and the other thing about the HIDs that if run AFCI on 3 phase system it can affect with harmoic effect i know i mean just a single circuit not the multi circuit and also the power factor capatiotrs i dont know it can throw the moneky wrench in there too.
but when the time go by more we will know more
merci, marc
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)
|
|
|
|
Joined: Feb 2004
Posts: 494
OP
Member
|
hi, HID lighting must be fed with HID rated breakers..per client request/specs..
there are no HID rated AFCI breakers available that I know of...unless someone else knows..
-regards
mustang
[This message has been edited by mustangelectric (edited 10-07-2004).]
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
Mustang: That only applies if the breaker is used as the switch. From the 2002, section 240.83 (D) Used as Switches. Circuit breakers used as switches in 120-volt and 277-volt fluorescent lighting circuits shall be listed and shall be marked SWD or HID. Circuit breakers used as switches in high-intensity discharge lighting circuits shall be listed and shall be marked as HID.
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Feb 2004
Posts: 494
OP
Member
|
Hi, sorry, i meant in the application i am working on..
the client specified ALL AFCI breakers for everything single pole..other than required gfi's
we were wondering what kind of trouble they were getting into..all i can say it is the very large retail company and i am sure there is a store of theirs in your neighborhood...big blue sign..installing fueling stations..everywhere..300+ next year..
thanks for the replies..very interesting..
mustang
|
|
|
|
Joined: Apr 2001
Posts: 518
Member
|
Next thing you know, some engineer will specify AFCIs in a welding shop...
|
|
|
|
Joined: Feb 2004
Posts: 494
OP
Member
|
thanks for the laugh...that was a good one..can i use that?
mustang
|
|
|
|
Joined: Jan 2004
Posts: 615
Member
|
And GFI your sacrificial cathode circuit...
|
|
|