I have installed a DSC PC1555 hard wire alarm system with a PC 1575 LED keypad after checking all wiring and allowing the back battery to fully charge I tried to get the system to operate. The "trouble" light appears with zone light 1 on which indicates "Service Required" I would like to know what needs to be done to allow the system to operate properly. No other lights come on indicating all other systems are working properly. Any assistance would be greatly appreciated. Thanks Mty Jerry
|
|
|
|
Joined: Nov 2000
Posts: 246
Member
|
Does this system need an end-of-line resistor installed?
Have you tried the company's tech support?
Good luck.
Rick Miell
|
|
|
|
Joined: Mar 2004
Posts: 251
Member
|
All zones must have EOL resistors installed including the fire zone. If not, you will have a trouble light. Also if the comunicator has been programmed and the phone line is not connected it will also show trouble.
|
|
|
|
Joined: Jun 2004
Posts: 220
Member
|
also ohm the zones at the panel for grounds, and the zone in question, ohm the pair and verify that you can " see" the EOL on the zone.
|
|
|
|
Joined: Dec 2001
Posts: 444
Member
|
Here is what you do :
Approach the keypad. Press * 2 The Zone that lights up indicates the trouble. If its Zone 1, then press "1" again. If its one of the other Zones see the chart : Here are the Zone codes :
Zone 1 - Service Required light 1) low battery light 2) bell circuit trouble light 3) general system trouble light 4) general system tamper light 5) general system supervisory light 6) not used Zone 2) AC failure Zone 3) Telephone Line Monitoring Zone 4) Failure to communicate Zone 5) Zone Fault Zone 6) Zone Tamper Zone 7) Device Low Battery (if you are using wireless) Zone 8) Loss of system time.
I am willing to bet you have 2 troubles. I think its the loss of system time. You must program the time in the system to work properly. And, I think you have TLM trouble. The manual explains how to disable the TLM, OR, run a phone line to the system so that it "see's" a dial tone.
End of line resisters are optional for this system. It can be disabled through programming if EOLs have NOT been used.
Please let me know how you make out.
|
|
|
|
Joined: Sep 2004
Posts: 2
OP
Junior Member
|
I have programed it for the time, date, etc. I will try to diaable the TLM as you suggest. I do have the phone connected and checked to make sure it was working properly. Thanks Jerry
|
|
|