#40766 08/03/04 02:30 PM
Joined: Jan 2003
Posts: 46
B
Big A Offline OP
Member
Doing a service change and the AHJ wants an outside disco. Does this mean I have to run a four wire system from the disco to the service panel? Doesn't this in effect make the service panel a sub-panel?

Sorry if this sounds like a DIY'ers question, it's not. I've just never done a service change where they required me to use a disco after the can.

#40767 08/03/04 03:22 PM
Joined: Oct 2000
Posts: 4,116
Likes: 4
Member
Big A,

Yes to both questions. They make Meter/Mains (Meter enclosures with a Main Breaker) that might be your easiest solution.

Bill


Bill