ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (gfretwell), 32 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
#40570 07/26/04 09:30 PM
Joined: Dec 2003
Posts: 524
Member
...Had an emergency call to a diner I do alot of work in,for an intermittently tripping breaker.Went to check it out,and the 20a.Square"D" tandem breaker was HOT to the touch.The breaker governs a refrigerator compressor and drew only 14.3amps.@ 120 volts,...still,the darn thing was hot.The system voltage is 120/208,and the sub-panel feeder is 200amps.I changed the breaker,rearranged the order so that I could put the compressor on it's own 20amp.,HACR rated breaker...Haven't heard from them since,...this was last Saturday.What could've been the problem?? A faulty breaker,??When it did trip,it went to "overload" status,by which,I mean tripped in the middle position,if it had been a short,or a locked rotor,the breaker would've tripped all the way off,...no??
At 14.3 amps,I can't see why it behaved that way...I'm baffled...Could an unbalanced panel load cause this??
I'm all out of theories!! HELP!!
Russ

[This message has been edited by Attic Rat (edited 07-26-2004).]


.."if it ain't fixed,don't break it...call a Licensed Electrician"
#40571 07/26/04 09:37 PM
Joined: Nov 2000
Posts: 2,148
R
Member
Russ,
The most common reason for "hot" breakers is a poor connection. It can be at the buss, the load conductor or even inside of the breaker itself.
Don


Don(resqcapt19)
#40572 07/26/04 09:44 PM
Joined: Apr 2002
Posts: 2,527
B
Moderator
Increased contact resistance in the breaker pole will manifest as excess heat from additional I²r loss. It may be too late to determine if the breaker has been taken out of service, but in-situ AC millivolt-drop tests can sometimes flush out the problem. See http://ecmweb.com/mag/electric_testing_contact_quality/index.html

Also, with a little care—similar measurements can be made at the wire/load-side connection and main bus/breaker line-side spring-clip connection.




[This message has been edited by Bjarney (edited 07-26-2004).]

#40573 07/26/04 10:48 PM
Joined: Apr 2002
Posts: 558
C
Member
I agree with Don and BJ. If the connection to the buss and to the branch wire was good it is probably bad contacts in the breaker. The trip position is the same for both thermal and magnetic.


Curt Swartz
#40574 07/27/04 05:30 AM
Joined: Jul 2004
Posts: 5
K
Junior Member
Russ, also, short circuit or overload, the breaker always trips to the middle position.

#40575 07/27/04 09:53 AM
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
How hot is hot?

The hottest spot of a circuit breaker is the operating handle.

Looking in a 1987 version of NEMA AB-1.
[The] Temperature-rise of various materials and parts;
Main operating means: (b) parts of insulating material - 60C [140F]
Main circuit terminals for external connections - 50C [122F].

Note: the handle rating is based on a temperature rise (increase) above an ambient of 25C (77F).

So even a properly functioning breaker, that is fully loaded, can be too hot to touch.

#40576 07/27/04 06:21 PM
Joined: May 2004
Posts: 186
A
Member
Russ, How about position of the breaker in relation to other loaded breakers, are you getting any heat transfer that is causing the tripping problem? You did say that you have rearranged the order, could the new position be cooler? Just a thought.
Good Luck.
Alan

#40577 07/27/04 07:15 PM
Joined: Jun 2004
Posts: 206
C
Member
Russ, I agree with BJ and Don. Look at the link BJ provoided. I use the millivolt drop test on breakers all the time. Readings approaching 100 mv toss the breaker and install a new one. This is one of the tests I do when doing Infarred work for my company.

Alan is also correct. Other loads around the tripping breaker can cause overheating.

Al

#40578 07/27/04 10:43 PM
Joined: Dec 2003
Posts: 524
Member
... Thanx all,...as usual,you guys were right there for me...JBD,the breaker was HOT,...and I believe that's what contributed to the tripping..Also,the surrounding breaker(s)could've been a heat factor as well...it definetly stopped tripping once I changed the breaker from a tandem to a single pole QO breaker,and relocated it in the panel..The case of the faulty breaker was melted a bit,and the sticker was singed..
I firmly believe that it was the breaker whose contacts may have been carbonized,and contact was poor... Thanx again guys,I'll keep you posted if anything else crops up.. [Linked Image] [Linked Image]
Russ



[This message has been edited by Attic Rat (edited 07-27-2004).]


.."if it ain't fixed,don't break it...call a Licensed Electrician"
#40579 07/28/04 09:45 AM
Joined: Jul 2001
Posts: 599
J
JBD Offline
Member
Russ,

I agree the breaker probably needed to be replaced. And definitely, the initial panel layout was poor. Remember the ambient air (actually the inside of the panel) around any one breaker needs to be below 25C (77F) or you will reduce it's current carrying capability.

My point was, the temperature of the breaker is not a major factor in troubleshooting a circuit. The behavior of the circuit is more important. If the breaker tripped whenever the compressor kicked in, then it was tripping magnetically. If it tripped after a few minutes of running then it was tripping on overload.

Square D QO breakers only have three positions On, Tripped, and Off. You can not tell what kind of event caused a QO breaker to trip.