#40209 07/18/04 03:35 AM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
Electricmanscott,
Not in my town....
If it requires tools to access the the plug, it fails 422.16!

Might be just another SF thing, but I never do it anywhere else either. The code wording is vague, but the way it's read around hear is typical to any appliance fastened in place, they read it as the same as 422.16B(2).

Stoves
Trash Compactors
Ovens
Dishwashers
Microwaves
What-ever, not just in the kitchen either.

Technically, anything with a cord, and screwed to a cabinet, or anything else.


Quote
422.16B(2)Built-in Dishwashers and Trash Compactors.

Built-in dishwashers and trash compactors shall be permitted to be cord-and-plug connected with a flexible cord identified as suitable for the purpose in the installation instructions of the appliance manufacturer where all of the following conditions are met.
(1) The flexible cord shall be terminated with a grounding-type attachment plug.
Exception: A listed dishwasher or trash compactor distinctly marked to identify it as protected by a system of double insulation, or its equivalent, shall not be required to be terminated with a grounding-type attachment plug.
(2) The length of the cord shall be 0.9 m to 1.2 m (3 ft to 4 ft) measured from the face of the attachment plug to the plane of the rear of the appliance.
(3) Receptacles shall be located to avoid physical damage to the flexible cord.
(4) The receptacle shall be located in the space occupied by the appliance or adjacent thereto.
(5) The receptacle shall be accessible.



[This message has been edited by e57 (edited 07-18-2004).]


Mark Heller
"Well - I oughta....." -Jackie Gleason
#40210 07/18/04 08:00 AM
Joined: Oct 2000
Posts: 5,392
S
Member
i hit two concerns w/ one circuit here.


Undercab lights, which are best single wire due to final movement/placement all make back to a 4/11 with single mud plate for a dup rec, behind the stove.

(i learned that here btw) [Linked Image]


as to hardwired appliances, check out those that have been so for 30 odd years, replaced along the way, remodeled around, etc....

you'll be sold on a non-electrician means of detachment...

~S~

#40211 07/18/04 08:18 AM
Joined: Jan 2002
Posts: 1,457
E
Member
The NEC seems to contradict itself in allowing a receptacle behind a dishwasher or trash compactor. "In the space occupied by the appliance or adjacent thereto". "Shall be accesible" As for other appliances every built in micro, I have been involved with specs the location for the recptacle. It is always behind the unit. Manufacturers instructions?

#40212 07/18/04 08:35 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
The cord does not have to be called the disconnecting means. [Linked Image]

If the unit has a switch marked off you are probably all set. 422.34

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#40213 07/18/04 10:17 AM
Joined: Dec 2003
Posts: 751
E
Member
422.16(B)(3) allows the receptacle supplying the counter-mounted cooking units to be connected by cord and plug. No mention of accessibility is included as it is for dishwashers and trash compactors.
It is permitted to cord and plug connect any counter-mounted cooktop, regardless of it's mounting hardware!


Earl
#40214 07/18/04 10:45 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Quote
Undercab lights, which are best single wire due to final movement/placement all make back to a 4/11 with single mud plate for a dup rec, behind the stove.

That is a great idea, even if you can get the placement right, getting 2 cables closed up in some under cabinet lights can be tough.

I have a job going now that I have six 'little inch' under cab lights to wire with 12/2 MC I also will have a JB but I have the option of installing it above the dropped ceiling.

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#40215 07/18/04 12:26 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
Found another code, more applicable to the orignial question, 422.33A+B

Quote
(A) Separable Connector or an Attachment Plug and Receptacle. For cord-and-plug-connected appliances, an accessible separable connector or an accessible plug and receptacle shall be permitted to serve as the disconnecting means. Where the separable connector or plug and receptacle are not accessible, cord-and-plug-connected appliances shall be provided with disconnecting means in accordance with 422.31.
(B) Connection at the Rear Base of a Range. For cord-and-plug-connected household electric ranges, an attachment plug and receptacle connection at the rear base of a range, if it is accessible from the front by removal of a drawer, shall be considered as meeting the intent of 422.33(A).

iwire, where do you put the switch, if you can't use the cord as disconnect? In the cab next to it...

Now I have put recepticals under stoves, 2' from the floor, for stoves that have spring held toe kicks. Simular to the way one would place the rerceptical for a Sub-Zero fridge. (that 6X9" square behind the unit) And micro's with spring held trim kits. (I have only seen one type made this way. panasonic)No tools...

As for under cab's I do the same thing, but also accessable, in the back of the lower cab's. For romex jobs the best item is the 2g adjustable box. Carlon zip box, I do the whole kitchen in them! They have a screw to adjust the depth on the side of the box, so you can get zero tolorance on the wood in the cab. Or, I guess the "Smart box" advertised on this site could work, I haven't used them... I wish they made the same in steel.


Mark Heller
"Well - I oughta....." -Jackie Gleason
#40216 07/18/04 12:51 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
E57 the unit switch(es) the ones on the front of the DW or range are allowed to be the disconnecting means if they meet the requirements of 422.34

That aside the requirements you posted 422.16(B)(2)(5) for example require the outlet to be accessible this is much different from readily accessible.

Quote
Accessible (as applied to equipment). Admitting close approach; not guarded by locked doors, elevation, or other effective means.

Quote
Accessible, Readily (Readily Accessible). Capable of being reached quickly for operation, renewal, or inspections without requiring those to whom ready access is requisite to climb over or remove obstacles or to resort to portable ladders, and so forth.

There is no reason the JB for the undercabs can not be behind the range.

The requirements for JBs are only accessible not readily accessible. [Linked Image]

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#40217 07/18/04 11:44 PM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
iwire,
We'll agree to disagree. But don't do it in SF, that I know for sure!


Mark Heller
"Well - I oughta....." -Jackie Gleason